Few days behind on this one, but yeah... the comments are all generally
correct regarding surge supression.
I'll share some thoughts...
The two most common ways to protect against surges on AC lines are
MOV's and gas-discharge tubes.
MOV's react sooner but can't withstand high current and will be
destroyed or damaged by high surges of current. Gas-discharge tubes
are slow to fire but can then pass (relatively) large amounts of
current.
Some very good designs (rare) use both... MOV's fire quickly at the
beginning of the surge event and start shunting unwanted voltage to
ground, then the gas-discharge tubes fire and soak up the rest of the
current. These designs last through just about anything other than
direct or indirect lightning strikes if the right values of the
components are used.
Many of the radio site systems I've worked with people on over the last
10 years or so have had their power supplies internally modified to
have both MOV's and gas-discharge tubes. In those last ten years, I've
seen about four complete MOV failures due to lightning either close-by
or a direct hit to the radio tower itself, even after proper lightning
protection (single point ground, halo systems, and Polyphaser panels at
all entrances to the building) has been followed. The gas-discharge
tubes rarely fail, but some have had signs of arcing over the tube and
into the power supply.
Since the one club's technical lead started adding these modifications
to the power supplies, no power supplies have been completely lost due
to lightning, however if the MOV's are completely destroyed by a hit,
the AC feed to the supply is broken and the radio system goes dead
until someone can arrive at the remote site and repair the MOV's and
check the gas-discharge tubes for damage.
Another effect we have here in Colorado is that electrolytic filter
capacitors in power supplies are prone to drying out -- and the caps
are sometimes in the front sections of the power supply as either
rectifiers or filters to help the supply provide "clean" power to the
system. Inside electrolytic capacitors is a liquid/jelly substance
that is the electrolyte the makes them work -- at high altitude in dry
climates like ours, 10 years of sitting in a non-environmentally
controlled building at 10,000-13,000' MSL will cause the water content
of the caps to become lower than their design tolerances allow and they
then either degrade in performance or in the worst case, arc over
internally and "pop", usually leaving a "strange" confetti-like
substance inside the case of the power supply and two attachment leads
soldered into the board with nothing attached to them anymore, or just
small pieces left-over.
Anywhoo... that's just some of the fun things I've seen working on
radios that live in harsh environments around here.
Cheap "power strip" surge protectors USUALLY only have MOV's in them...
thus, if you think your store-bought surge protectors have survived a
big surge... it's probably time to replace them. As Dan mentions, many
designs do lay in an LED across the MOV to show that it's still capable
of passing current, but it does not prove that the MOV is still acting
normally or "firing" at the same place in the curve after a big surge.
Best to just chuck out the $10 surge suppressor and put in a new one at
that price... or at least find a suitable replacement MOV and change
them out if you suspect yours have been put through a large surge.
The number one rule in lightning "protection" that I've read and can
back up with experience of having seen the damage after a number of
direct strike incidents, is that you want your ground system to rise
and fall for every device in the system at the same potential. Older
houses with multiple grounds (water pipe ground to a sub-panel in the
basement, outside ground rod, telephone ground rod, ground rod at a
detached garage - i.e. My 1960's house... oh no!) that are not directly
bonded together suffer the worst from external surges.
Lightning strikes nearby and instead of the ground system becoming
instantaneously charged to a specific potential and then tapering off
as the system discharges through the single-point ground, the system
"sees" each ground as a better or worse place to discharge -- and then
high current flows between the grounding points... thus causing major
damage in the house wiring (or other conductive paths like appliances
and other household electronics) between the grounds.
Hope that's helpful info. Boiled down it is:
- MOV's generally fail after surges - replace surge suppressors that
have been "hit".
- Designs with gas-discharge tubes can offer greater protection but
slower response.
- Think about your grounding system. (Example: Putting a metallic
power strip with a surge suppressor inside of it into your 7' data
center rack and then expecting it to do any good is foolish... the
MOV's inside drop the excess voltage and current to the CASE GROUND of
the power strip... which is touching the metal rails of your cabinet...
thus, energizing the cases of all the machines in the cabinet. Oops.)
Oh... almost forgot...
Inexpensive consumer-grade UPS's are typically "off-line" type designs.
This means that they sense a loss of power and THEN kick over to the
battery, faster than the downstream power supplies will notice. This
also means that in many cases these cheaper UPS's do little or no
actual surge suppression, depending on their design. Many only have
MOV's similar to a "regular" surge suppressor. Some people think that
having a UPS is a good way to protect equipment because the batteries
themselves act as slow capacitors and can help absorb transients -- but
that's only true in the case of so-called "on-line" UPS's.
Okay... 'nuff said... probably too much. ;-) Heh. Sorry.
--